In our previous article we saw how you can configure a utility network to perform isolation traces for gas and water networks. In that article we saw how the system can identify equipment that can be used for isolation, along with how to configure our network to use a normal position field to identify whether a valve is open or closed. In this article we will show you how to configure a utility network to manage pressure zones. The examples outlined in this article are for a gas network, but the techniques and concepts are applicable to any pressurized network.

What is a pressure zone?

An important part of managing the distribution of resources to customers in a pressurized system is the creation and analysis of pressure zones. The engineers at a utility rely on complex formulas and engineering software to ensure the system operates as intended, however, they often rely on the network model stored in a GIS to build these models. It is the responsibility of a GIS analyst to ensure that the data in the GIS is kept up-to-date and accurate so engineers, planners, and network operators can make informed decisions using GIS.

Pressure zones play an important role in the daily responsibilities of operators and engineers. For operations and engineering to use GIS, they must have confidence that it contains an accurate accounting of the features regulating and belonging to each pressure zone. Read the Understanding Pressure Zones article to learn how to use GIS to manage and analyze pressure zones.

Historically, customers have maintained pressure zone information as an attribute on pipes, or by using a polygon layer in their GIS that shows the extent of each zone. This information may look good on a map but doesn’t work in cases where there are multiple pressure zones on the same street or when a user inadvertently creates a connection between pipes in different pressure zones. Scenarios such as this are where a utility network provides value, since it can be configured to model and validate the extents of pressure zones.

The utility network created using the Migrate To Utility Network tool can include a single tier for managing distribution systems by default. These large groupings of pipes all share a common source of gas, water, or energy. To assign a pressure zone to a pipe, we need to configure a tier to represent the pressure zones. If your domain network is configured to be partitioned each feature can only belong to a single tier, so you must choose between tracking the system tier or pressure zones. Gas, water, and district heating domain networks are typically modeled using a hierarchical network for this reason. Hierarchical networks allow each feature to participate in multiple tiers in the network. This is not limited to systems and pressure zones either. Some customers also use GIS to track isolation zones, cathodic protection structures, or even district metered areas.

When adding a new tier to a utility network, you need to ask yourself the following questions:

  • What is the purpose of this tier?
  • What features govern or regulate (sources or sinks) this tier?
  • What features are allowed to belong to this tier?
  • Are there any statistics I want calculated for the subnetworks in this tier?

With this information in hand, you are ready to start configuring a new tier. The first step is to configure certain features to act as the sources or sinks in the tier. In the utility network, these features are called subnetwork controllers.

Subnetwork Controller Configuration

Before a feature can act as a subnetwork controller, its asset type must be configured to act as a subnetwork controller in a tier in the network. You can find a full list of the steps on the set a subnetwork controller page in the online help, but we will cover them briefly here.

  1. Assign a terminal configuration
  2. (optional) Delete previous rules
  3. Add rules
  4. Assign a network category
  5. (optional) Add a tier
  6. Set the subnetwork definition

If you have already identified the equipment that impacts flow or pressure as subnetwork controllers when you ran the Migrate To Utility Network tool, then your asset types are already configured to act as subnetwork controllers, and you can skip ahead to adding a tier.

To start, we need to assign a terminal configuration to the asset types we want to be assigned as subnetwork controllers. When a line connects to a device with terminals, it must specify which terminal it is connected to. The ability to differentiate between connections is required when creating subnetwork controllers. As an example, without the use of a terminal configuration and terminal connections, a regulator would be unable to distinguish between the pipes connected to its inlet and the pipes being regulated connected to its outlet.

The Migrate To Utility Network tool includes three generic terminal configurations:

  1. Directional Source – This terminal configuration is used when a device in a source-based network needs upstream and downstream terminals.
  2. Directional Sink – This terminal configuration is used when a device in a sink-based network needs upstream and downstream terminals.
  3. BiDirectional – This terminal configuration is used when there is no explicit upstream or downstream terminal. It can be used in either source or sink-based networks.

Picking the right terminal configuration is important to ensure that tracing works properly. In a pressurized system, most network controllers have an explicit upstream and downstream terminal configuration. This means that water, gas, etc. can only flow from the pipe on the upstream terminal to the pipe on the downstream terminal. However, if you have equipment that can be configured to not regulate flow in the field you should use the BiDirectional terminal configuration which will allow pressure to be unregulated as it flows through the device. In our example, we will be configuring our device to be BiDirectional because several of our regulator stations maintain a high-pressure loop in our distribution system.

RobertKrisher_0-1741623660222.pngRobertKrisher_0-1741623660222.png

Note: If this tool is run using ArcGIS Pro 3.5 or later, you will need to remove any existing rules associated with the asset type using the Delete Rule tool before you can set its terminal configuration.

Once you have changed the terminal configuration of the device, you then need to create rules that allow you to define which types of pipes are allowed to connect to either terminal. In this example regulator stations have distribution pipes on both the inlet and outlet side of the device, so you will add rules for each side.

RobertKrisher_1-1741624256119.pngRobertKrisher_1-1741624256119.png

Note: When a pipe is allowed to connect to more than one terminal on a device, each pipe must specify which terminal it is connected to on the device. If it does not, this creates an ambiguous connectivity error that must be resolved using the Modify Terminal Connections tool.

If you were adding rules for town border stations or custody transfer meters, you would only allow transmission pipe to be on the upstream terminal and distribution pipe on the downstream terminal. If you are uncertain of which rules to add, consult with an engineer or someone else with an understanding of your system to help you make the right decision.

In the case of water models, pumps or pressure reducing valves would have distribution pipes on both the upstream and downstream terminals.

Now that the regulator in our example has terminals which allow it to differentiate between the pipe connections on either side, you can begin to configure it as a subnetwork controller. The next step is to assign a network category to the asset type to allow it to serve as a subnetwork controller. To do this, use the Set Network Category tool:

RobertKrisher_1-1741623699388.pngRobertKrisher_1-1741623699388.png

The next step is to define what kind of subnetworks the device is allowed to act as a subnetwork controller for using the Set Subnetwork Definition tool. The device should serve as a subnetwork controller for pressure zone subnetworks, but first a tier must be created to represent the pressure zones first. This is done using the Add Tier tool.

Adding a pressure zone tier

Now that your asset types have the network category, terminals, and rules to act as network controllers you’re ready to add your tier to the network. Use the Add Tier tool to add a new tier to the network.

RobertKrisher_2-1741623755504.pngRobertKrisher_2-1741623755504.png

You can learn more about these settings on the Tiers topic in the online help. Because our utility network already contains a tier for the distribution system, which has the default rank of 1, we set the rank of pressure zones to be 2. This means that pressure zones are deeper in the network hierarchy than our system subnetworks.

Because we already have a field that stores our system subnetwork name, we specify a new field called PressureSubnetworkName to store the name of the pressure zone. Don’t worry about creating this field ahead of time, the tool will automatically add the field for you.

Now that we’ve added a pressure zone tier to our network, we need to define the features that act as subnetwork controllers and participate in the subnetwork, along with the rules of how the subnetwork trace should be performed. To do this we use the Set Subnetwork Definition tool. This tool has quite a few parameters, so it is recommended that you read the subnetwork definition page in the online help before running this tool on your network.

For the Valid Features and Objects section, we specify all the asset types in our network with just a few exceptions.

For the Valid Subnetwork Controllers parameter, we only select our regulator stations and any other equipment we configured to act as subnetwork controllers for pressure zones.

RobertKrisher_0-1741623780578.pngRobertKrisher_0-1741623780578.png

The Aggregated Lines for Subnetline Feature Class parameter is used to identify which lines are used to create the subnetwork line geometry when the update subnetwork operation is run. Because this line is used to visualize pressure zones when zoomed out to small scales, we don’t want to include any asset types that contain many small lines. In the case of our pipe system, we don’t want to include any services, laterals, or lines used exclusively for cathodic protection.

RobertKrisher_1-1741623808240.pngRobertKrisher_1-1741623808240.png

Note: Features excluded from the subnetwork line are still considered when calculating summaries for the subnetwork.

Because your network doesn’t include structures or nonspatial content, you will want to disable, or uncheck the options to include containers, content, and structures. You will also want to treat open devices as barriers using a condition barrier, just as you did with the system tier.

RobertKrisher_2-1741623808241.pngRobertKrisher_2-1741623808241.png

Don’t worry about populating summaries when first setting your subnetwork definition. You can change your subnetwork definition later to include summaries about things like pipe length, volume, and number of service connections.

The aggregated lines for subnetline feature class parameter is used to identify which lines are used to create the subnetwork line geometry when update subnetwork is run. Because this line is used to visualize pressure zones when zoomed out to small scales, we don’t want to include any asset types that contain many small lines. In the case of our pipe system, we don’t want to include any services, laterals, or lines used exclusively for cathodic protection.

Update Subnetwork Policy

RobertKrisher_3-1741623832080.pngRobertKrisher_3-1741623832080.png

The last major section to configure for the subnetwork definition is the update subnetwork policy. This gives you control over how subnetwork information is updated within your utility network. Making changes to these settings is not a simple decision for many customers, as it involves making tradeoffs between convenience and performance. We will give a brief overview of these decision points here and refer you to more thorough discussions where available.

RobertKrisher_4-1741623832081.pngRobertKrisher_4-1741623832081.png

If you chose to include containers, content, and structures in your network, additional options will be displayed for you to specify whether to update structure/domain network containers. This determines whether the Subnetwork name and Supported subnetwork name attribute fields on your structures and containers will be updated when they contain or support a feature that belongs to a subnetwork. This allows you to use the Select By Attributes tool to identify features that support a subnetwork without running a trace. While this is convenient for reporting purposes, it also means that the update subnetwork operation will take longer to run because there may be hundreds of thousands of additional features that need to be updated.

RobertKrisher_5-1741623858547.pngRobertKrisher_5-1741623858547.png

The next option to discuss is whether the tier should manage the IsDirty (Status) field, you can find a deep dive on state management on the Esri Community site. This field is used to indicate whether there have been edits validated in your utility network that have impacted a particular subnetwork. This option is set to False by the Migrate To Utility Network tool because it can have performance impacts.

When this property is enabled, the utility network must perform one or more traces to identify which subnetworks are impacted every time you validate edits, The performance cost is relative to the size of your largest pressure zone. If you have pressure zones that contain hundreds of thousands of features (pipes, junctions, and devices), you should keep this parameter disabled. However, if all your pressure zones are smaller than that, you may consider waiting a few additional seconds during the validate network topology operation to be a relatively small cost compared to the benefits to quality assurance. If you are not sure which option to choose, you should leave this property disabled until you are confident about the size and performance impact of your pressure zones. This option should almost always be set to false for system tiers, since they can easily contain your entire dataset.

Having this property enabled allows you to focus your quality assurance efforts on just the subnetworks that have been modified and allows you to easily identify which circuits have been clean and ready to be extracted to an external system like an OMS.

The most performant configuration is to leave this option disabled. The configuration that is most beneficial for quality assurance and integrations is to enable state management.

RobertKrisher_0-1746017676582.pngRobertKrisher_0-1746017676582.png

The last option to consider is which eventing mode to use for your default and for named versions. This decision affects the performance of update subnetwork and whether the subnetwork field is populated during certain workflows. There is a deep dive on eventing modes on the Esri Community site. A greatly simplified version of the discussion follows.

When a subnetwork is updated without events it will run faster. There are several factors that contribute to this, but one reason is that attribute rules and editor tracking are not triggered. The largest drawback to this behavior is that when updating subnetwork in a named version, not all features are guaranteed to have their subnetwork name updated to match the subnetwork they belong to.

When a subnetwork is updated with events, the first time the update subnetwork operation is run it will take longer than those which follow.  Subsequent updates may also take longer to update if you have attribute rules configured and are updating large numbers of features. The benefit of updating subnetworks with eventing enabled is that when update subnetwork is run in a version you can guarantee that the subnetwork name feature is correctly populated for all the features belonging to that subnetwork.

Note: Starting with ArcGIS Enterprise 11.4 and ArcGIS Pro 3.4, the performance cost of triggering attribute rules can be mitigated using the new Triggering Fields behavior of attribute rules.

The most performant configuration is to leave the eventing mode to update without events. The most useful configuration for quality assurance is to enable the eventing mode when in named versions and to ensure you have properly configured triggering fields on all your attribute rules. When you are working in a mobile or file geodatabase the recommended setting is to update without eventing, since this allows you the first and subsequent runs of update subnetwork to run quickly as you work through your connectivity and quality assurance issues.

Enabling subnetwork controllers

Once you’ve done this, the last remaining step is for you to identify the subnetwork controllers for each pressure zone in your system. To do this you will need to visit every subnetwork controller in your network (in this example regulator stations) and use the Modify Subnetwork Controller pane to associate each terminal on the device with the respective pressure zone on either side. If you have ambiguous connectivity errors on your device, you need to use the Modify Terminal Connections pane before enabling the subnetwork controller to ensure you are enabling the correct terminal as a subnetwork controller.

When starting this process, it can be difficult to know where to start, since you may have dozens or hundreds of pressure zones. This is further complicated when one pressure zone is nested inside another pressure zone. The temptation is often to begin as the highest-pressure pressure zones at the center of your system and work your way outwards, the problem with this approach is that as soon as you create your first pressure zone it will consume all downstream and nested pressure zones because those subnetwork controllers haven’t been configured to regulate pressure yet. Instead, it is often easier to begin creating controllers at the edges of your system and work your way inwards. In this way you don’t need to worry about nested zones, and if you make a mistake, you likely only need to investigate the connections with one or two neighboring pressure zones.

RobertKrisher_0-1741623899417.pngRobertKrisher_0-1741623899417.png

If you zoom into the regulator station on the western side of the service territory you can see that the inlet/outlet of this regulator isn’t immediately obvious. However, deciphering this can be made easier by turning on labels for the set pressures of each pipe.

RobertKrisher_0-1741624120536.pngRobertKrisher_0-1741624120536.png

Similarly, it helps to look at the terminal each line is connected to. In fact, when creating subnetwork controllers, you should always verify that the terminal connections between your controller and device are correct. If they are not properly set this will cause problems when you trace your subnetworks. You can see the terminal connection using the Modify Terminal Connections pane on each connected line or, if you’re particularly clever, you can create a label class on the layer to show this information.

RobertKrisher_1-1741623919340.pngRobertKrisher_1-1741623919340.png

RobertKrisher_2-1741623919341.pngRobertKrisher_2-1741623919341.png

Because you assigned a BiDirectional terminal configuration, the terminals are specified as  Side 1 and Side 2. If you had a directional terminal configuration you would want to see the 720 psi pipe on the upstream terminal and the 60 psi pipe on the downstream terminal. Now that you are confident in the terminal connections of our regulator, you can create the subnetwork(s). Use the Modify Subnetwork Controller pane on the regulator to create a subnetwork for the 60 psi pipe.

RobertKrisher_3-1741623937116.pngRobertKrisher_3-1741623937116.png

Ensure the tier is set to Pressure Zone and select the terminal connected to the 60 psi pipe. Because a subnetwork can have multiple controllers, you need to uniquely identify this subnetwork controller. If you have a unique name field you can use, put it here, otherwise you can leave this blank and the system will use the feature’s global id. Finally, put the name of the pressure zone in the subnetwork name field.

Once the terminal has been enabled as a subnetwork controller, you must validate the network topology for the feature before it can be used.

RobertKrisher_4-1741623952686.pngRobertKrisher_4-1741623952686.png

After validating the topology, you can then use the trace tool to trace the subnetwork and validate the correct result is returned.

RobertKrisher_5-1741623952689.pngRobertKrisher_5-1741623952689.png

Once you’ve verified it traces correctly, use the Update Subnetwork tool to create the subnetwork for the first time.

RobertKrisher_6-1741623952691.pngRobertKrisher_6-1741623952691.png

Once the subnetwork has been successfully updated, you can use the Find Subnetworks pane to visualize the subnetwork. This pane can also be used to trace, update, and review the status of your subnetworks.

RobertKrisher_7-1741623974293.pngRobertKrisher_7-1741623974293.png

 

Once you’ve repeated this process for all your pressure zones you should repeat the quality assurance processes you followed for systems to ensure that every feature is associated with the correct pressure zone.

Conclusion

In this article you learned how to configure your utility network to model subnetwork controllers for pressure zones. You learned about the configuration required to allow a feature to be a subnetwork controller, along with how your subnetwork definitions affect the behavior of your system.

Now that you’ve created pressure zones for your data you can use them for many kinds of analysis. If you’re looking for inspiration, check out the Understanding Pressure Zones article. Your configuration journey doesn’t have to end here. If you’re looking for more things to configure, consider the following:

  • Run isolation traces using the new pressure zones
  • Create trace configurations using your pressure zones
  • Add summary functions to your subnetwork definitions (pressure or system tier)
  • Review the eventing and state management configurations of your pressure tier

If you want to know more about using the utility network to manage pressurized networks, like gas and water systems, please explore the Learn ArcGIS Utility Network for Water Utilities and Learn ArcGIS Utility Network for Gas and Pipeline learning series. This learning series includes tutorials and articles that demonstrate how to address the needs of these industries using the utility network.