Our Electrical UN has these rules about connections allowed to Elbows:

BryanMay531_0-1747342916250.png

Yet, We have connections to Elbows with None for terminal settings and no errors:

BryanMay531_1-1747343048449.png

and :

BryanMay531_2-1747343129323.png

These rules should ensure terminal must be set, right?  (I swear they were being enforced recently)

0 Kudos
1 Solution

Accepted Solutions
MikeMillerGIS
Esri Frequent Contributor

The rules show that a 3 phase primary can only connect to line side, since there is not an ambiguous rule, an explicit terminal connection is not required, as the rules define that is can only connect to the one line and not the other.

View solution in original post

8 Replies
MikeMillerGIS
Esri Frequent Contributor

The rules show that a 3 phase primary can only connect to line side, since there is not an ambiguous rule, an explicit terminal connection is not required, as the rules define that is can only connect to the one line and not the other.

BryanMay531
Regular Contributor

So should it be an error when 3phase primary is snapped to the elbow and terminal is set to none?

0 Kudos
BryanMay531
Regular Contributor

Oh. So are you saying it is assumed to be line side because that is the only acceptable terminal?

0 Kudos
MikeMillerGIS
Esri Frequent Contributor
Correct
0 Kudos
BryanMay531
Regular Contributor

Awesome!  Thanks. I love this system!

0 Kudos
RobertKrisher
Esri Regular Contributor

@BryanMay531 If we didn't have this behavior, you would have to explicitly set the terminal connections for every transformer in your system, which would make editing your conductors tedious.

It makes sense that you wouldn't need to populate the terminals for your elbows, since the line side should always be connected to a conductor/cable and the bus side should always be connected to the bus work.

Your rules may not be as clear cut, depending on your drawing standards. If you allow an elbow can be drawn with buswork or conductor on BOTH sides of the elbow THEN you will need to have rules allowing for this and will need to explicitly populate terminals on each line.

0 Kudos
BryanMay531
Regular Contributor

Thanks Robert,  I think I get it.  I did all of our development with the full UN model so got in the habit of setting everything.  When we went to production I removed a ton of stuff and didn't realize the change.  So if I delete ambiguous rules I can get this behavior on other features right?  Currently rules allow MV Connectors and conductors to snap to either side of Elbows and then the terminals must be set.  But we only want connectors on bus side and conductors on line side.  But if I remove the rules for the unwanted connections then we won't have to set them anymore.  If I understand this correctly?

 

0 Kudos
RobertKrisher
Esri Regular Contributor

@BryanMay531 That is correct. If you always have bus on a particular terminal and conductor on the other terminal, setting your rules so there isn't ambiguity means that you don't need to explicitly populate/manage the FromDeviceTerminal and ToDeviceTerminal fields on lines.