Hi,

I'm using the Gas and Pipeline Referencing Utility Network Foundation v.2.1 to model parts of a gas utility.

I'm trying to determine subnetworks in the Pressure Tier. The controllers (regulators) switch from high to low pressure correctly, but when I update the subnetwork with the geoprocessing tool the flow is "blocked" by the Pipeline Device "Decoupler". 

lorenzoz_0-1673969767184.png

The Decoupler is topologically connected to the pipes and is listed as a valid device in the networks options for the pressure tier. The Lifecycle status is set to In Service. I tried changing the Decoupler from DC to AC, still doesn't work.

I need a Decoupler because I need a point that refences a stop in the flow of current. 

Am I missing something? 

Thank you in advance,

Lorenzo

0 Kudos
1 Solution

Accepted Solutions
MikeMillerGIS
Esri Frequent Contributor

A Decoupler has a category of CP Only.  I would suggest removing this category

MikeMillerGIS_0-1674062517686.pngMikeMillerGIS_1-1674062528236.png

 

View solution in original post

0 Kudos
2 Replies
MikeMillerGIS
Esri Frequent Contributor

A Decoupler has a category of CP Only.  I would suggest removing this category

MikeMillerGIS_0-1674062517686.pngMikeMillerGIS_1-1674062528236.png

 

0 Kudos
lorenzoz
Occasional Contributor

Thank you Mike for you answer! I will try unissign the category

Lorenzo