In an electric grid having a section of the grid de-energized due to open switching devices between it and one or more subnetwork controllers I need Utility Network to offer a trace telling me potential switching devices to close in order to re-energise this section.

At Esri UC 2024 I discussed this with David Crawford and he suggested an approach that could bring me some of the way, yet may output false positives.

Let me explain.

  1. I place a trace starting somewhere in the de-energised section and initiate a Connected trace.

  2. This connected trace is configured with Condition Barrier Operating Status Normal equals Open
    Jens_Dalsgaard_0-1721264308967.png

    This will make the connected trace stop at open switching devices.

  3. and with Output Condition also set to Operating Status Normal equals Open
    Jens_Dalsgaard_1-1721264350479.png

    This will make the connected trace only return these open switching devices.

  4. And it does return open switching reachable from the trace starting point placed within the de-energised section of the grid. So far so good.

  5. Yet, in case of loops within the de-energized section or open switching devices to a customer currently disconnected the trace result will include open breaker not allowing in-feed. False positives.
  6. You guys, Esri, have the entire graph model in the background and I assume it's feasible for you guys to offer a trace capability / configuration returning only the open breakers which upon closing would in fact re-energise the section in question without including false positives.

Looking forward to your answer and fix.